Boatdreamer,
Your comment that caught my attention is, "...The Mase 2.7 just keeps humming along just fine, but the A/C won't start back-up for awhile."
That statement suggests that the A/C starts working again on its on after some time period. If this is true, then I suspect you have an icing issue. Assuming you have the Dometic A/C, check out this section of the Passport I/O Digital Control (for DX systems) manual - Dometic Marine Rev. 20091102 L-2231 English:
"P-8: De-Icing Cycle
The de-icing cycle prevents ice build up on the evaporator coil during extended periods of cooling operation. Installation variables such as grille sizes, length of ducting, insulation, and ambient temperatures determine the run time required to achieve set point. Factors that substantially increase run time include operating the system with hatches and doors open, and programming an unrealistic set point (e.g. 65°F/18.3°C). Such situations can cause the evaporator to form ice on warm humid days.
• For software revision A13 and older, de-icing is accomplished by switching the reversing valve into Heat Mode while the system is cooling. The valve remains energized for the programmed cycle time. The cycle is programmable to “OFF” or to a period of 1, 2, or 3 minutes.
• For software revision A21 and newer, de-icing is accomplished by closely monitoring the room air temperature in 10-minute intervals during a cooling cycle. Depending on the parameter value and the change in room temperature during these monitoring intervals, the control performs various actions to prevent ice from forming or to melt ice that has already formed. This is accomplished by short compressor shutdown periods combined with a one-speed increase in fan speed, and by periodic Heat Mode cycles with the fan turned off.
The parameter setting for the de-icing feature depends on whether you are using the optional alternate air-temperature sensor or the display’s built-in room air-temperature sensor. Installation of an optional alternate air temperature sensor (located in the return air path) greatly increases the effectiveness of the de-icing feature, and this option should be considered whenever the display sensor cannot read the room temperature accurately.
• If using an optional remote air-temperature sensor, set this parameter to “1” to turn the de-icing feature on, or to OFF to disable.
• If using the display’s built-in room air temperature sensor, this feature has two selectable behavior modes. Both modes attempt to compensate for any temperature discrepancy the display sensor experiences. (Although discrepancy is not typical, installation variables such as where the display is placed inside the room—near an open door or in direct sunlight—can affect how accurately it reads the actual room temperature.) Set this parameter to “1” to assume the display sensor may be reading the room temperature as much as 5°F (2.8°C) greater than the actual evaporator temperature (standard). For more extreme installations, set this parameter to “2” to assume the display sensor may be reading the room temperature as much as 7°F (3.9°C) greater than the actual evaporator temperature. The setting of “2” should only be used if a setting of “1” does not prevent evaporator ice from forming."