I agree with John on this subject. First confirm that the boat is wired properly before installing a isolator to fix a problem. Once it is confirmed the boat wiring is 100% ABYC compliant and you want to protect your boat and its electrical system more install a isolation transformer.
This is a copied statement from the ABYC Blog.
The only AC neutral to ground (connecting the white wire to a green wire) connections on board are made at generators or inverters, and then only when they are invert mode. Additionally, if the boat is equipped with an
isolation transformer, then the boat side of the transformer becomes a new source of AC power and therefore a neutral to ground link is established.
This is the same thing that is done when using a Honda Generator onboard. The Neutral and ground can be combined by using a special plug that links the neutral to ground at the source (Honda Generator)
I took a Look at the
Bridgeport Magnetics Isolation Puck, installation
https://www.bridgeportmagnetics.com/wp- ... scaled.jpg
There is no ground/'neutral connection at the isolator. The new source which is normally done based on the ABYC requirement. Without this bond you will see the polarity light on which as been already concluded by Osprey.
This is the design of this isolation puck. Here is a description from the.
ISO-PUCK isolation transformers do not feature output Neutral to Ground Bond. They provide a true floating system (IT Earthing System) for maximum protection against excessive ground leakage current.
Kaptajnen":ocry3u4u said:
He spent several hours trying to troubleshoot this, including calls to Bridgeport Magnetics technical guy, but was not able to solve this conundrum.
I'm surprised that the ABYC certified electrician and the technician from Bridgeport did not realize this. No bond of neutral and ground at the isolator the panel reverse polarity light will be on.
Wee Venture":ocry3u4u said:
This is because the light is measuring voltage between the neutral and ground wires: if they are bonded together at the source it should be zero, or very close to it. If it is unbonded and left to float, you can get a voltage differential due to capacitive coupling or leakage.
Based on this installation your reverse polarity light will remain on. I would run this by the manufacture and the ABYC electrician that this is considered ABYC compliant. I would assume it is if they make this devise for boats.